"Forum on Risks to the Public in Computers and Related Systems" <"Peter G. Neumann" Tue, 8 May 2007 10:58:28 PDT This is another example of a system environment in which components that were supposedly not safety related could compromise safety. The case is of considerable interest to RISKS. On 19 Aug 2006, operators manually scrammed Browns Ferry, Unit 3, following a loss of both the 3A and 3B reactor recirculation pumps, as required after the loss of recirculation flow -- which placed the plant in a high-power, low-flow condition where core thermal hydraulic stability problems may exist at boiling-water reactors (BWRs). Generally, intentional operation is not permitted under this condition. Although some BWRs are authorized for single loop operation, sudden loss of even one pump could present the plant with the same stability problems and could result in the reactor protection system initiating a shutdown of the plant. [Source: Effects of Ethernet-based, Non-safety Related Controls on the Safe and Continued Operation of Nuclear Power Stations, United States Nuclear Regulatory Commission, Office of Nuclear Reactor Regulation, Washington, DC 20555-0001, 17 Apr 2007; PGN-ed, although the following text is abridged but unedited.] The initial investigation into the dual pump trip found that the recirculation pump variable frequency drive (VFD) controllers were nonresponsive. The operators cycled the control power off and on, reset the controllers, and restarted the VFDs. The licensee also determined that the Unit 3 condensate demineralizer controller had failed simultaneously with the Unit 3 VFD controllers. The condensate demineralizer primary controller is a dual redundant programmable logic control (PLC) system connected to the ethernet-based plant integrated computer system (ICS) network. The VFD controllers are also connected to this same plant ICS network. Both the VFD and condensate demineralizer controllers are microprocessor-based utilizing proprietary software. The licensee determined that the root cause of the event was the malfunction of the VFD controller because of excessive traffic on the plant ICS network. Testing by site personnel performed on the VFD controllers confirmed that the VFD control system is susceptible to failures induced by excessive network traffic. The threshold levels for failure of the VFD controllers due to excessive network traffic, as determined by the on-site testing, can be achieved on the existing 10-megabit/second network. The NRC staff's review of industry literature and test reports on network device sensitivity, and the threshold levels for such failures, confirmed these testing results. The licensee could not conclusively establish whether the failure of the PLC caused t... [ Read More (0.5k in body) ] |