Browns Ferry 3 nuclear power site scrammed
by unmanaged at 9:09 pm EDT, May 24, 2007

"Forum on Risks to the Public in Computers and Related Systems"
<"Peter G. Neumann"
Tue, 8 May 2007 10:58:28 PDT

This is another example of a system environment in which components that
were supposedly not safety related could compromise safety. The case is of
considerable interest to RISKS.

On 19 Aug 2006, operators manually scrammed Browns Ferry, Unit 3, following
a loss of both the 3A and 3B reactor recirculation pumps, as required after
the loss of recirculation flow -- which placed the plant in a high-power,
low-flow condition where core thermal hydraulic stability problems may exist
at boiling-water reactors (BWRs). Generally, intentional operation is not
permitted under this condition. Although some BWRs are authorized for
single loop operation, sudden loss of even one pump could present the plant
with the same stability problems and could result in the reactor protection
system initiating a shutdown of the plant. [Source: Effects of
Ethernet-based, Non-safety Related Controls on the Safe and Continued
Operation of Nuclear Power Stations, United States Nuclear Regulatory
Commission, Office of Nuclear Reactor Regulation, Washington, DC 20555-0001,
17 Apr 2007; PGN-ed, although the following text is abridged but unedited.]

The initial investigation into the dual pump trip found that the
recirculation pump variable frequency drive (VFD) controllers were
nonresponsive. The operators cycled the control power off and on, reset the
controllers, and restarted the VFDs. The licensee also determined that the
Unit 3 condensate demineralizer controller had failed simultaneously with
the Unit 3 VFD controllers. The condensate demineralizer primary controller
is a dual redundant programmable logic control (PLC) system connected to the
ethernet-based plant integrated computer system (ICS) network. The VFD
controllers are also connected to this same plant ICS network. Both the VFD
and condensate demineralizer controllers are microprocessor-based utilizing
proprietary software.

The licensee determined that the root cause of the event was the malfunction
of the VFD controller because of excessive traffic on the plant ICS network.
Testing by site personnel performed on the VFD controllers confirmed that
the VFD control system is susceptible to failures induced by excessive
network traffic. The threshold levels for failure of the VFD controllers due
to excessive network traffic, as determined by the on-site testing, can be
achieved on the existing 10-megabit/second network. The NRC staff's review
of industry literature and test reports on network device sensitivity, and
the threshold levels for such failures, confirmed these testing results. The
licensee could not conclusively establish whether the failure of the PLC
caused t... [ Read More (0.5k in body) ]


 
 